> Drive the rod into the ground by your service panel/terminal block and run the ground lines into whatever room your using
Please don't do that.
Power-pole transformer shorts hot to neutral. The neutral rises to 120V, or even 13,000V. In your scenario, it finds Ground by going through your equipment to the dirt-rod. This is very unsafe.
The proper legal way is to ground outlets to the fusebox, and ground the fusebox to dirt. Then most stray power runs directly to dirt, not through your gear or you.
In a house that was wired in the 1920s, there is a good chance that all the wire is run in metal conduit, rigid or flex. In theory, and in old code, that metal conduit is ground. You can install 3-pin outlets and jumper the green screw to a screw or clip on the box. There are even special outlets with grippers on the mounting screws so you can trust the mounting screw to bond to the box (even if the screw is not too tight).
In fact the center screw on outlets is generally considered to "be ground".
In recent code, the fact that flex-conduit is a pretty crummy ground is recognized. In new work, you use new flex with a grounding strap inside, or run an actual groundING conductor back to the fusebox.
But assuming this is not a kitchen or bath, and that this is a small studio, I would simply take one 2-pin outlet through a 2-pin/3-pin adapter (using the ground screw if possible) to several 3-pin power-strips. In most cases, if everything on the system is on the same "ground", it works fine even if that ground is not connected to the rest of the world.
A "power conditioner" is usually something else. It stabilizes wobbly voltage (lights dim and brighten), and diverts spikes to the other side of the line or to ground. If your lights burn steady, and you don't have hash when the elevator or A/C kicks-in, there is not a big need for this. As as describe above, when the really big spikes (power-pole or lighting hits) arrive, often you are in better shape with everything floating than with it in the path to ground.
If you are in kitchen or basement (concrete conducts better than your body), don't fool around with your life. Get a proper legal to-Code ground conductor if at all possible, and also use a GFI shock-preventer (these are legal and effective even where there is bo groundING wire).