I believe the situation is properly described in
http://en.wikipedia.org/wiki/Earthing_system
http://en.wikipedia.org/wiki/Earthing_system
If it is a really safe ISO xfmr (less than 120pF leakage capacitance), you could dispense with the ground, but I would not recommend it anyway.jwhmca said:There isn't a lot of space in the thing. I'm not thinking I could fit a transformer in there... If I made a External ISO transformer and made the two go together, would I still need to ground the chassis, like in my second picture (RED Mark)?
Neutral and ground connected at SE/panel.Speedskater said:For a US type AC power system, then general rules are:
a] The only place the Hot and Safety Ground (EGC/PE) are connected together is at the building Service Entrance /main circuit breaker box.
b] The Safety Ground must be securely connected to the chassis. No tack soldering.
c] The power switch must be on the Hot. If both the Hot & Neutral are switched, then it must be an interlinked switch.
d] The fuse must be on the Hot.
JohnRoberts said:Neutral and ground connected at SE/panel.Speedskater said:For a US type AC power system, then general rules are:
a] The only place the Hot and Safety Ground (EGC/PE) are connected together is at the building Service Entrance /main circuit breaker box.
JR
ricardo said:I think Neutral & Gnd are connected together at the Distribution Substation where zillion kV Delta distribution is converted to 230V Star. Your house gets one of the phases and the GND/Neutral (the Star point).
I don't think you connect Neutral & Gnd at the Service Entrance (your house main circuit breaker box).
This means I ALWAYS expect a few VAC between Neutral & Gnd in a properly wired UK/Oz house.