I have an oil fired heating system thats in its own seperate boiler house , inside the house by the fuseboard is the timer which originally switched mains power to the burner and hot water pump .
Just lately I've had a fault ,elcb tripped out , I tested the wiring with an insulation tester(1000v range), 3kohms between live and neutral ,11kohms between neutral and ground . I have already run an auxillary mains supply to keep the heating going , but I have to go out to the boilerhouse to plug in or out to switch on or off .
Just as a test I applied 9volts from a cell across my now disconnected neutral and ground wires out to the boiler , sure enough despite the bad insulation 9volts appears at the other end with little or no current draw .
I'll just provide +12vdc to the contacts on the timer and down the dodgy cable and use another relay in the boiler house to switch the mains supply from a nearby 16 amp outlet.
At 12volts I can easily afford the 1.2ma of current the poor insulation resistance of the cable costs me , even if the cable degrades further ,it still only consumes a fraction of what the relay does.
I was looking at the wifi theromostatically controlled radiator valve systems .It comes as a package usually with 5 motorised valves ,I like the idea in some ways ,but I dont want any of the phone apps or computer based crap , just a simple control panel . Does anyone have experience of these ?
Just lately I've had a fault ,elcb tripped out , I tested the wiring with an insulation tester(1000v range), 3kohms between live and neutral ,11kohms between neutral and ground . I have already run an auxillary mains supply to keep the heating going , but I have to go out to the boilerhouse to plug in or out to switch on or off .
Just as a test I applied 9volts from a cell across my now disconnected neutral and ground wires out to the boiler , sure enough despite the bad insulation 9volts appears at the other end with little or no current draw .
I'll just provide +12vdc to the contacts on the timer and down the dodgy cable and use another relay in the boiler house to switch the mains supply from a nearby 16 amp outlet.
At 12volts I can easily afford the 1.2ma of current the poor insulation resistance of the cable costs me , even if the cable degrades further ,it still only consumes a fraction of what the relay does.
I was looking at the wifi theromostatically controlled radiator valve systems .It comes as a package usually with 5 motorised valves ,I like the idea in some ways ,but I dont want any of the phone apps or computer based crap , just a simple control panel . Does anyone have experience of these ?