> Sure would help to have a schematic.
Couple places (oddly both in Canada) who will sell or rent(!) manuals for similar models (like a "B" instead of a "BB").
> This is starting to scare me...
Very good idea. These beasts ARE dangerous.
But 1,400V, even CT, is odd for a 325V output. Taking 100V across the 6L6, 100V across the rectifier, the raw B+ might be 525V. For cap-input filtering (choke-input is almost impossible for a supply that is often run with no load) that says maybe 400V each winding (800VCT).
Generally these things worked much like the Heathkit. Start with +500V, drop voltage in big tubes(s). To a first approximation, the output voltage is the same as the big-tube(s) grid voltage. In fact the grid has to be held negative of the cathode and output. So if the output is asked to go to +325V, the big-tube grids have to be pulled to ~+300V; to go to Zero volts, the big-tube grids have to be pulled to -25V or so. This pulling around is done by the voltage amplifier, a small tube. Its output terminal is always positive of its grid or cathode, so to get its plate down to -25V, its cathode has to be tied to a large negative voltage. -150V in the Heath. So we need a negative supply in addition to the big positive supply for the main output.
The symptoms suggest that somehow the "center", where positive and negative supplies come together, has been "lost". So it looks like one extra-big positive supply. It is not clear to me where the fault would be.
The burnt part should be a clue (and yes, if it burnt, you need a replacement at least as large!). But a resistor won't burn-up unless something else is wrong. Maybe a prolonged overload, now long gone, but these boxes typically stood great abuse without failing. Replacing the resistor and watching it burn-up again might lead you to the fault. But I assume the markings are burned-up, so you don't know what to replace it with. With a mostly-complete schematic, we could probably guess the function and value.
Couple places (oddly both in Canada) who will sell or rent(!) manuals for similar models (like a "B" instead of a "BB").
> This is starting to scare me...
Very good idea. These beasts ARE dangerous.
But 1,400V, even CT, is odd for a 325V output. Taking 100V across the 6L6, 100V across the rectifier, the raw B+ might be 525V. For cap-input filtering (choke-input is almost impossible for a supply that is often run with no load) that says maybe 400V each winding (800VCT).
Generally these things worked much like the Heathkit. Start with +500V, drop voltage in big tubes(s). To a first approximation, the output voltage is the same as the big-tube(s) grid voltage. In fact the grid has to be held negative of the cathode and output. So if the output is asked to go to +325V, the big-tube grids have to be pulled to ~+300V; to go to Zero volts, the big-tube grids have to be pulled to -25V or so. This pulling around is done by the voltage amplifier, a small tube. Its output terminal is always positive of its grid or cathode, so to get its plate down to -25V, its cathode has to be tied to a large negative voltage. -150V in the Heath. So we need a negative supply in addition to the big positive supply for the main output.
The symptoms suggest that somehow the "center", where positive and negative supplies come together, has been "lost". So it looks like one extra-big positive supply. It is not clear to me where the fault would be.
The burnt part should be a clue (and yes, if it burnt, you need a replacement at least as large!). But a resistor won't burn-up unless something else is wrong. Maybe a prolonged overload, now long gone, but these boxes typically stood great abuse without failing. Replacing the resistor and watching it burn-up again might lead you to the fault. But I assume the markings are burned-up, so you don't know what to replace it with. With a mostly-complete schematic, we could probably guess the function and value.