earthsled said:
Let me back up for a moment.
In an ideal situation (when the 48V supply has a dedicated secondary winding), where should 0V of the 48V PSU be connected? Should it go the "big bolt" chassis connection described earlier, or is there a better location for the connection?
That is the right question to ask. The basic rule is that the chassis and cable screens should not carry 0V. So you connect screens to the chassis and connect the 0V to the chassis at one point (the big stud) only as discussed earlier.
Trouble is, phantom power
breaks these rules because its signal 0V
is the screen of the mic cable which we should connect direct to the chassis. But this means we are potentially connecting a 0V to the chassis at a
second point which is a recipe for ground loops.
The solution has to be a compromise and there are two choices.
1. Connect mic XLR pin1 to chassis at the XLR and connect phantom power 0V to chassis at the big stud. The problem with this is that
all the interference currents from
all sources flowing in the chassis to the big stud are now flowing in our mic input 0V - we don't really want
all interference currents flowing in perhaps the most sensitive 0V in the whole system.
2. Connect mic XLR pin1 to chassis and run a separate phantom power 0V up to the mic inputs and bus it along the pin 1 connections with a thick piece of copper wire. Any interference current flowing in the mic cable screen also flows in the phantom 0V but that is all and there is nothing we can do about them - the mic input common mode rejection is supposed to take care of that sort of thing. All other interference currents flow down the chassis to the big stud and do not induce current in the phantom 0V.
So what I do is option 2. I connect all the mic XLR pin1s to the chassis at the point of entry and I connect them all together with a neavy guage copper wire. I connect the phantom power 0V to the centre of this copper wire and nowhere else.