That's a good point. Medical iso xfmrs are usually less than 120pF stray capacitance.I would have to look and see if there are some makers mrks on it. It came from a hospital installation.
That's a good point. Medical iso xfmrs are usually less than 120pF stray capacitance.I would have to look and see if there are some makers mrks on it. It came from a hospital installation.
I didn't realize before that the ground electrode system bus is not connected to neutral at all in this diagram. So it's not just fault currents from the RCBOs that will go to the ground rod, it's fault currents of all breakers.
Here's a pic of the beast. It's so heavy it puts me absolutely on the limit to pick it up. Question, it there a way to measure the stray capacitance without being in a physics lab ?That's a good point. Medical iso xfmrs are usually less than 120pF stray capacitance.
Not very easy, because the actual capacitive effects are capacitance from primary to core, capacitance of secondary to core and capacitance between primary and secondary. The specified capacitance is the latter, but the others are larger.Here's a pic of the beast. It's so heavy it puts me absolutely on the limit to pick it up. Question, it there a way to measure the stray capacitance without being in a physics lab ?
What are fault currents from breakers?So it's not just fault currents from the RCBOs that will go to the ground rod, it's fault currents of all breakers.
That's why I implied that they don't flow from the breakers.RCD and GFCI can operate properly with only two active connections (line and neutral). It doesn't matter where stray currents flow, only that they are not flowing in the correct conductors.
Fault current that is ultimately sourced from a breaker. So it's not just currents sourced from the RCBOs that will fault to the ground electrode system. Current sourced the MCBs also will fault to the ground electrode system. Meaning there's nothing special about RCBOs in this respect. But I'm getting the feeling I'm the only one that missed that so ... carry on.What are fault currents from breakers?
My understanding is that fault currents are related to circuits.
....With 230 Volts incoming to the RCD it will not 'trip when the test button is pressed. Bought a new one and that also won't trip when tested. Brought the original RCD home and it works fine on the bench with 230 Volts applied....
presumably line and neutral are connecting to the RCD, if I understand no load is connected downstream but utility breaker (RCD?) still trips.Had a strange day here. Trying to #=unravel a mystery for a friend. Electrics fine for 2 years but a lightning strike in the locale a few days ago. NOW ONE of the 30ma tripping RCDs is acting strangely.
the premises has 4 30 milliamp breakers and a 'master 500 Milliamp (electric company master breaker/switch.
The 500 milliam main trips after a couple of minutes if ONE of the 30 MilliampRCDs is switched ON (but the load breakers are OFF so ONLY the NEUTRAL is actually connecting.
no bueno... The trip test is shunting current around the sense loop to create imbalance. Not test tripping is a huge red flag warningWith 230 Volts incoming to the RCD it will not 'trip when the test button is pressed.
If the 500mA mains trips without loads connected that suggests to me the problem may be close to that and/or upstream.Bought a new one and that also won't trip when tested. Brought the original RCD home and it works fine on the bench with 230 Volts applied.
Cooker is fed PRE the 30 milliamp RCDs (and (incorrectly so is the socket used for kettle).
Now trying to work out how wiring that has been working for 2 years is now 'incorrect as it seems the Neutrals (wired to UK 'code') are crossed somewhere as it seems something is picking up a Neutral from the 'wrong' RCD. WHY the 'fault' takes about 1 or 2 minutes to trip the master 500 milliamp RCD is just part of the mystery. Must be 'wine time'.
Identifying the 40 or more blue Neutrals and pairing them with respective lives is a project for another day. The Neutral is wandering around about 3 Volts above 'Earth (well the bar with some green/yellows on it) but the limit is 10 Volts to allow for resistive drops in the Neutral from where the electric company bond them.
No. in most cases, the fault current comes fom the live wire touching a earthed body. Unless seriously damaged, the breaker does not leak current.Fault current that is ultimately sourced from a breaker.
Very often, the fault current doesn't flow to the ground rod (spike). When you touch the live wire and you're standing on a tile floor, current goes to earth in a very diffuse way that completely ignores the ground rod.So it's not just currents sourced from the RCBOs that will fault to the ground electrode system. Current sourced the MCBs also will fault to the ground electrode system.
Of course.Meaning there's nothing special about RCBOs in this respect.
To me it's a sign the leak is pretty low, so the magnetic does not detect, but the thermal does.WHY the 'fault' takes about 1 or 2 minutes to trip the master 500 milliamp RCD is just part of the mystery.
Of course. What was I thinking?To me it's a sign the leak is pretty low, so the magnetic does not detect, but the thermal does.
Thanks a good thought BUT as the 500mA breaker is happy to supply the cooker AND kettle (about 8 Amps each Both separately and together, for the duration of the test, I can't see it being the thermal part as such.
My point, perhaps not blunt enough, was that posting information about UK electrical safety from a site outside of the UK (in this case Serbia, but would be equally at issue were it USA, France, Germany, wherever) from an unknown organisation with content of dubious origin and correctness, doesn't really help a thread on a safety-related topic. Each country has its own electrical codes for a variety of reasons, so you cannot compare safety earthing systems unless treading very carefully.P.S.
I hope this site I linked isn't hosted in Serbia.
I can only imagine what a shame it would be if it is hosted in Croatia.