Thanks, we seem to be confusing multiple topics...So earth is not connected to neutral in an RCBO breaker? That is odd. In that case fault current would go through the earth ground electrode, through soil to neutral at the utility pole. Probably not a good arrangement for a studio.
Update:
Actually it looks like any imbalance (Residual Current Breaker with Overload) will trip it. So as long as the earth ground electrode impedance isn't too high, EGC doesn't need to be connected to neutral for safe operation.
View attachment 92150
Indeed GFCI/RCD protection devices do not need to be ground bonded to work, these devices simply compare the current flowing in the two active conductors (typically Line and Neutral) and trip open circuit if they don't null out. The GFCI per outlet protection uses a trip threshold of only 6 mA imbalance, RCD branch circuit protection requires more like 30mA imbalance. The RCBO is an RCD + conventional overload breaker making these suitable for use in mains breaker panels to replace old school overload only breakers.
These devices do not care where the missing current goes, only that it isn't flowing where it should be....
[TMI] Back several years ago when I was messing around with designing a premium talent protector I combined a GFCI outlet with a 3 pole relay so in addition to opening the line conductor, I opened all three circuits. My logic was that live performance talent shock hazards include external energized voltage sources exposing the talent to hazard conducting through a still present safety ground. In my premium protector I sensed current flow through the safety ground path and opened all three conductors at 6mA or more current in the ground.
It is clearly debatable wether a robust safety ground "could" ever be a shock hazard. I didn't even bother trying to convince UL, they like their safety ground bonds. It is not unusual for talent to get shocks from grounded microphones that provide a return path for external energized sources. [/TMI]
JR