I recall the UL being picky about things labelled as "ground".... patchbays, not so much.
JR
JR
Yes, gas and water lines must also be connected to building ground.
I have only worked on systems within a single building, but as Bill Whitlock (Mister CMRR) has pointed out to me in the past, because anything metal is connected to the building grounding conductor, if you have something like a patch bay in a commercial building, the exposed metal has to be connected to building ground. That is why the XLR cabling standard still has pin 1 for shield connection which is not connected to the connector shell in cables, so that when the cable shell is grounded by a patch panel connected to building metal, you do not get multiple connections of a cable shield to building ground on a long connection going between buildings, or between different electrical service entrances in a really large building.
I fail to see the logic of earthing a patchbay for safety or regulatory reasons
cable shields are not safety grounds... UL ground bonding tests drive on the order of 50A though a "ground" path and measure the voltage rise... many shields will fuse open at 50A.Relying on cable shields for safety grounds is dangerous (= fuse to ground), as is not having all ground systems inside the same facility being properly bonded together.
yupEvery piece of equipment in a studio system (that is not some POS with a 2 prong power cord) should have it's power cord complete with a ground pin connected to a properly grounded outlet.
yupPower cord ground lifts are NEVER the correct way to deal with a ground problem such as a ground loop.
can't quite follow what you said..There are cases where the power cord ground is not bonded to the internal P/S ground (as in a power supply to a console where the P/S commons tie to ground at the console, and this P/S common is properly terminated to Technical Ground using the console's ground lug). In the "good ole days" many manufacturer's included a ground bond strap on the back of equipment for this purpose... but inside individual pieces of equipment this is a poor solution to a shielding / physical mounting fault.
BTW, "Everything goes to the console, and it goes to the ground rod" IS a Star Ground system. Of course it is only safe if that ground rod is bonded to all other ground systems in the facility.
busThe reasons why moving the bonding point for the main ground buss
ground is a concept... audio signals are differential audio + wrt audio -....to the audio system from being tied to the Neutral at the panel to being bonded to the end of a series of ground rods that the panel (& conduit & Neutral bond) is bonded to often vastly lowers the noise floor of an studio system may be debatable, but the results are not. This is standard practice in "isolated ground" systems such as Hospitals and large computer facilities, where the conduit (system safety) ground and the 3rd pin ground are kept separate and are only bonded at this point.
Even better, a "2 hots & a ground" system (balanced AC power or 2 phase) solves the voltage on the Neutral problem nicely.
Of course, any piece of audio gear will turn on and pass signal without being grounded, but that does not mean it is safe or predictable, and as stated elsewhere, shielding and CMMR performance are improved with proper grounding.
I am certainly not working on a super-collider in my basement, but I hope all of us here understand enough basic physics to be able to safely implement audio systems and get great results from them!
Did anyone suggest that?Relying on cable shields for safety grounds is dangerous
and you were doing so well.BTW, "Everything goes to the console, and it goes to the ground rod" IS a Star Ground system. Of course it is only safe if that ground rod is bonded to all other ground systems in the facility.
Never ever do this.The reasons why moving the bonding point for the main ground buss to the audio system from being tied to the Neutral at the panel to being bonded to the end of a series of ground rods
BTW, "Everything goes to the console, and it goes to the ground rod" IS a Star Ground system.
Here, the subject is making a system as clean as possible.Of course it is only safe if that ground rod is bonded to all other ground systems in the facility.
Just to be clear if people like me had trouble parsing this - if the load touches the chassis the fault current will flow through earth ground of the mains cable back to the panel, into the neutral bus and not to the ground electrode.Safety ground provides a low-impedance (low enough to cause a high fault current to trip a breaker) path back to NEUTRAL, not earth ground.
Bo, you should proofread this sentence.Just to be clear if people like me had trouble parsing this - if the load touches the chassis the fault current will flow through earth ground of the mains cable back to the panel, into the neutral bus and not to the ground electrode.
Presumably we're just mixing up terms. Mains wiring is most commonly referenced as:Bo, you should proofread this sentence.
What "load" touches the chassis? Why this chassis would be live?
"Earth ground of the mains cable" does not make much sense.
In my area, it's "E". Never G.Ground / Earth / Protective Earth most commonly referred to as ground with letter 'G'
Actually it looks like "E" is more common. The most common is the earth ground symbol "⏚" but "PE" is also used.In my area, it's "E". Never G.
not to be more pedantic than usualPresumably we're just mixing up terms. Mains wiring is most commonly referenced as:
L typically refers to "line"Live / Hot and frequently has a letter of 'L' which I might be confusing with "load" instead of "live" perhaps
Correct but UL tends to also refers to neutral as a line conductor.Neutral which has letter 'N'
EGC (equipment grounding conductor) aka safety ground. The EGC is bonded to neutral at the panel to provide an adequate current path to trip breakers from voltage faults. UL calls it a grounding pin (grounding conductor) as compared to the line blade(s) in a plug.Ground / Earth / Protective Earth most commonly referred to as ground with letter 'G'
correctamundo...So restated, if the live conductor touches the chassis the fault current will flow through the ground conductor of the mains cable back to the panel, into the neutral bus and not to the ground electrode.
I just opened up a UL specification (S-1436) that I paid hundreds of dollars for when designing my outlet tester.Still a problem?
EGC? Effective Ground-Fault Current Path? 2 birds?So restated, if the live conductor touches the chassis the fault current will flow through the ground conductor of the mains cable back to the panel, into the neutral bus and not to the ground electrode.